Xenta 555 – Configuration of the Ethernet Communications settings.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Xenta 555 – Configuration of the Ethernet Communications settings.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1490 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Xenta 555 – Configuration of the Ethernet Communications settings.

Picard Product_Support
‎2018-09-07 11:50 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:29 AM

Issue

Xenta 555 –Configuration of the Ethernet Communications settings, using HyperTerminal.

Environment

Connection to the site Ethernet network

Cause

A requirement to change the Ethernet connection settings

Resolution

This operation will allow the user to modify the settings, as detailed below.

 

  • Connect the laptop to the Xenta RS-232 port B, using the RJ45-to-RJ10 Cable and DB9/Female-to-RJ45/Female Adaptor.

 

  • Run HyperTerminal on the laptop and configure as follows;

 

Run Hyper Terminal and configure as: -

Baud             9600

Data bits       8

Parity            None

Stop Bits       1

Flow Control   None

 

Press ‘Enter’ to display activate the command prompt.

 

Xenta555 Website name…    Session-id: xxxxxxxxxxxxxxxxx

Enter the Username: root

Enter the Password: root

At the prompt - Dsh/> - Enter setip

 

DHCP Yes/No  As appropriate (A fixed IP address is easier)

IP Address     As appropriate

Subnet Mask  As appropriate

Default Gateway       As appropriate (This would be the address of the main network router, it will be the same as the PC uses)

Dns     xxx.xxx.xxx.xxx (Again, if it is used then it will be the same as the PC uses)

Website Name   As required (This can be entered now, or downloaded via Xbuilder)

Domain Name  (Used for information only)

Host Name     (Used for information only)  

Change Root password yes/no        no

Do you want to restart the IP Interface. yes/no        yes

After configuring the 555 controller details, Enter: Dsh/>restart

 

The above information is also available in the TAC Xenta 500/700/911/913 Product manual, section 2.2.2.

Labels (2)
Labels:
  • Satchwell MicroNet
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4412
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore