Xenta 121-FC/HP not building terminal load in unoccupied night setup
  • Xenta 121-FC/HP not building terminal load in unoccupied night setup
  • Cody_Failinger
    Cody_Failinger
‎2018-09-10 05:05 AM
The Xenta 121-FC/HP controller will not build a terminal load when in unoccupied night setup mode.
  • ZBuilder 5.1.6
  • Xenta 121-FC
  • Xenta 121-HP
The “Cooling interlocked to fan” setting prevents the unit from building cooling terminal load in unoccupied mode.
This issue will be corrected in a future upgrade but for now this is a work around.
  1. Open ZBuilder
  2. Go to the Configuration tab > Control > Fan > Interlock
  3. Uncheck the box called “Cooling interlocked to fan”.
  4. Click Apply at the bottom of the window to update the settings in the controller.
  • 6834