Issue
XIF and Device Resource files for the Schneider Electric SE7000 Series Room Controllers
Product Line
EcoStruxure Building Expert, Field Devices, TAC IA Series
Environment
SE7000 Series Room Controller
Cause
In order to commission Schneider Electric SE7000 Series Room Controllers into an LNS system, the XIF is required.
Resolution
LonWorks External Interface Files (XIF)
- SE72_73_PIR.XIF (80:00:10:55:00:04:04:20)
- SE76_PIR.XIF (80:00:10:55:00:04:04:21)
- SE76RH_PIR.XIF (80:00:10:55:00:04:04:22)
Device Resource File for XIFs listed above.
For Datasheets for the SE7000 Series Controllers, see Where to find datasheets and information on the SE7000/SE8000 series room controllers.