XBuilder will not allow a connection between a third party LON device and a graphic

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • XBuilder will not allow a connection between a third party LON device and a graphic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • SESA128463
    SESA128463
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1903 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

XBuilder will not allow a connection between a third party LON device and a graphic

Picard Product_Support
‎2018-09-10 12:53 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 10:41 PM

Issue

Cannot connect network variable point from a third party LON device to a graphic within an XBuilder project. 

XBuilder will not allow the drag and drop of LON network variable between the network pain and the system pain when you attempt to create connections.

Product Line

EcoStruxure Building Operation, TAC Vista

Environment

  • XBuilder
  • Vista
  • Lon Device
  • .xif

Cause

XBuilder is very particular about the format of an .xif file and it will not allow certain characters in the function block name. Vista and LonMaker have far less limitations and these programs are able to parse these characters without causing problems. This explains why your values may show up in the LNS management tool and Vista Workstation. However, once you import the network into XBuilder you are unable to connect the SNVTs to your graphic.

Resolution

Replace the incorrect characters in the function block line of the .xif and reload the new .xif into your LonWorks Network.  Please see LON device can communicate in Vista, but fails in a Xenta Server / XBuilder for more information about incorrect characters in an xif file.

INCORRECT FUNCTION BLOCK EXAMPLE:

File: MP580.XIF generated by NODEUTIL Revision 1.46, XIF Version 4.0
Copyright (c) 1997 by Echelon Corporation
All Rights Reserved. Run on Fri Oct 31 16:30:28 2003

80:00:2A:52:00:03:04:03
2 15 1 618 0 8 8 4 4 11 11 0 0 0 0 3 0 16 0 0 1 65536 618
0 0 0 0 0 0 0 0 0 0 0 0 10000000
1 7 1 0 4 4 4 15 200 0
78125 0 0 0 0 0 0 0 0 0 0 0
0 0 0 0 0 0 0 0 1 5 8 5 12 14 15
*
"&3.4@0,20000-MP580,8500-SCC,8610-DAC

The problem is the three dashes  between the object numbers and the object names in the self doc string.  This is "allowed" in Vista and LonMaker in some sense.  For  example, Vista "replaces this "-" to a "/" but then XBuilder can't handle this situation properly.

CORRECTED EXAMPLE:

File: MP580.XIF generated by NODEUTIL Revision 1.46, XIF Version 4.0
Copyright (c) 1997 by Echelon Corporation
All Rights Reserved.  Run on Fri Oct 31 16:30:28 2003

80:00:2A:52:00:03:04:03
2 15 1 618 0 8 8 4 4 11 11 0 0 0 0 3 0 16 0 0 1 65536 618
0 0 0 0 0 0 0 0 0 0 0 0 10000000
1 7 1 0 4 4 4 15 200 0
78125 0 0 0 0 0 0 0 0 0 0 0
0 0 0 0 0 0 0 0 1 5 8 5 12 14 15
*
"&3.4@0,20000MP580,8500SCC,8610DAC;Tracer MP580

The dashes 3 x (-)s have been removed from the function block name

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (3)
  • Find more articles tagged with:
  • 11189
  • graphics
  • objects
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore