Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Workstation initialization registry entries and SQL queries to get Workstation parameters in an existing database

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Workstation initialization registry entries and SQL queries to get Workstation parameters in an existing database
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Alan_Wood
    Alan_Wood
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1978 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Workstation initialization registry entries and SQL queries to get Workstation parameters in an existing database

Picard Product_Support
‎2018-09-06 01:48 PM

Issue

As a last resort when a Cyberstation is offline or there are difficulties connecting to a database, it is necessary to change the Workstation Initialization fields using the Windows registry.

Environment

  • Continuum
  • Windows XP
  • Windows Vista
  • Windows 7
  • Windows Server 2003
  • Windows Server 2008

Cause

Partial objects in a database and registry entries occasionally get out of sync.

Resolution

Caution! Editing of the registry can be potentially dangerous, make sure someone who is familiar with using regedit completes this procedure. It is best to get a restore point of the Windows PC, if the version allows, prior to taking the following steps.

  1. Shutdown Cyberstation
  2. From Windows, Start> Run> Regedit Expand the hives(folders) to HKEY_LOCAL_MACHINE\SOFTWARE\Andover Controls
  3. Right Click on Andover Controls and select export, name the file and save. (This file can be used to restore the original settings of this branch) Expand the folder to HKEY_LOCAL_MACHINE\SOFTWARE\Andover Controls\Continuum\Settings
  4. Double click on Workstation Name (Change this to the name required Ex. WS1) Double click on Network Id and select decimal (Change value data to the number needed Ex. 192)
  5. Double click on Device Node Id and select decimal (Change value data to the number needed Ex. 192)
  6. Double click on Container Name (Change this to the name required Ex. WS1folder)
  7. Close Regedit
  8. Go into database initialization and select Workstation and you will now see those settings there. Go to the database tab and enter in the password for andover97 and click Ok. If the database initialization screen comes back(resolves to the database)with no errors, then this new instance of the Workstation was successfully created in the database.
  9. Launch Continuum

Note: On a 64- bit system the registry location is slightly different.

HKEY_LOCAL_MACHINE\SOFTWARE\WoW6432Node\Andover Controls\Continuum\Settings

 

Continuum queries to get some of the Workstation Initialization parameters (Comments in parenthesis are not part of the query)

select  * from device  (Device is the table name, uiname is the column where the Workstation Name can be found)

select * from container (Container is the table name, uiname is the column where the Folder Name can be found)

select * from device (Device is the table name, networkid is the column where the Network ID can be found)

Device ID is not available, but is often the same as the Network ID

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 5225
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore