Workstation Crashes when accessing Xenta Schedule link from Graphic Page
  • Workstation Crashes when accessing Xenta Schedule link from Graphic Page
  • RobertAndriolo
    RobertAndriolo
‎2018-09-07 02:35 PM
When trying to open the schedule, the attached crash report occurs and shuts down workstation with the following Exception message.
  • Object reference not set to an instance of an object
SmartStruxure 1.4.x
Menta application within the Xenta device has blank Exception Events defined with one or more Time Schedule blocks.
This will be corrected in a future release but as a workaround simply remove any Exception Event within the Xenta Time schedule block (TSCH).
Edit the block and set the Max. setting of the Exception Event to 0 (zero).  Save the application and download to the device.