Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Launch of Consumer/Home Owner registration process!
We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.

WorkPlace Tech Lon communication configuration for use with EBO.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • WorkPlace Tech Lon communication configuration for use with EBO.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • chris_clerc
    chris_clerc
  • Leo_Tantalo
    Leo_Tantalo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3654 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

WorkPlace Tech Lon communication configuration for use with EBO.

Picard Product_Support
‎2018-09-10 10:26 AM

Last Updated: Guinan RandyDavis Guinan ‎2023-09-11 01:57 AM

Issue

When using an Echelon U10/U20 USB or other Lon network adaptor for communication with a laptop and standalone WorkPlace Tech, not WorkPlace Tech Editor, you must change the default configuration settings.  The default Lon Network Domain ID length (1 byte), Domain ID (18 decimal) and Subnet (254) in the AS-P conflicts with the defaults used by WorkPlace Tech.

Product Line

TAC IA Series, EcoStruxure Building Operation

Environment

  • I/A Series WorkPlace Tech (Lon Network communication settings)

  • Building Operation Automation Server Premium

  • Building Operation Enterprise Server

Cause

Lon Network configuration

Resolution

  1. Look at the LonWorks Network "Advanced" tab in the AS-P to determine the addressing information.
    Lon_1.png
  2. Open the WorkPlace Tech WorkStation Communication Settings and select LonWorks.  Open the Change Address window
    Lon_2.png
  3. Select the "Manual Setup" radio Button
    Lon_3.png
  4. Modify to match the AS-P Lon Works Network configuration.  If a different Domain ID or subnet has been assigned in the AS-P, it will need to be assigned the same in WorkPlace Tech
    Lon_4.png
    Lon_5.png
  5. You can now browse the LonNetwork from the laptop.  If the MNL devices are assigned applications from the AS-P, do not modify the programs from the WorkPlace Tech Tool

 

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 19534
  • RandyDavis20
Was this article helpful? Yes No
100% helpful (7/7)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore