Issue
WorkPlace Commissioning Tool configured for BACnet IP is unable to discover MNB MS/TP devices connected to an ENC
Environment
I/A Series G3 Enterprise Network Controller BACnet Integration
Cause
The ENC station's BACnet routing is not enabled.
Resolution
In the G3 station, navigate to BacnetNetwork > Bacnet Comm > Network. Check and ensue that 'Routing Enabled' is set to true.