Wiring details when connecting an ARA 659 Esbe actuator to a Satchwell CZT 5305 controller.
  • Wiring details when connecting an ARA 659 Esbe actuator to a Satchwell CZT 5305 controller.
  • sesa139513
    sesa139513
  • sesa125819
    sesa125819
‎2018-09-11 06:31 AM
Connecting an ARA 659 Esbe actuator to a Satchwell  CZT 5305 controller.
Esbe
ARA 659
ARA 600 Series
Wiring
Confirmation of the actuator wiring connections to the controller.
The actuator is connected as follows;
CZT 5305 - Esbe ARA 659 actuator.
Terminal 36/37 - 24 volts (Brown wire).
Terminal 35 - 0 volts (Blue wire).
Terminal 19 - 0-10 volt (Black wire).- Heating actuator.
Terminal 20 - 0-10 volt (Black wire).- Cooling actuator.
To review the CZT 5305 datasheet please click HERE.
To review the ARA 600 series datasheet please click HERE.