Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Launch of Consumer/Home Owner registration process!
We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.

While opening a TGML graphic in webstation a security warning dialog box appears: 'Java has discovered application itemsthat could indicate a security concern.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • While opening a TGML graphic in webstation a security warning dialog box appears: 'Java has discovered application itemsthat ...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Jonas_Brissman
    Jonas_Brissman
  • Product_Support
    Product_Support
  • sesa120146
    sesa120146

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
887 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

While opening a TGML graphic in webstation a security warning dialog box appears: 'Java has discovered application itemsthat could indicate a security concern.

Picard Product_Support
‎2018-09-06 01:10 PM

Issue

While opening a TGML graphic in webstation a security warning dialog box appears: 'Java has discovered application itemsthat could indicate a security concern'.

Environment

Webstation 5.1.X
Java 6 update 19 and newer

Cause

Signed Java Web Start applications and applets that contain signed and unsigned items could potentially be unsafe unless the mixed code was intended by the application vendor. As of the Java SE 6 Update 19 release, when a program contains both signed and unsigned items, a warning dialog is raised.

Resolution

Mixed Code Protection Options for Users:
User can manage how mixed code programs are handled through the Java Control Panel.
To access the Java Control Panel goto, Start menu > Control Panel > Java Control Panel > Advanced > Security.
The following screen shot shows the four levels of control available. See the Mixed code heading towards the bottom of the Java Control Panel.


Below are the details of the available options.

  1. Enable - show warning if needed.This is the default setting. When a potential security risk is encountered, a warning dialog is raised. Clicking Yes blocks potentially unsafe items from running and may terminate the program. When the user clicks No, the application or applet continues execution with protections (packages or resources that are later encountered with the same names but have different trust levels, i.e., signed vs unsigned, will not be loaded).
  2. Enable - hide warning and run with protections.This option suppresses the warning dialog. The code executes as if the user had clicked No from the warning dialog.
  3. Enable - hide warning and don't run untrusted code.This option suppresses the warning dialog and behaves as if the user had clicked Yes from the warning dialog.
  4. Disable verification.This option is not recommended. This option completely disables the software from checking for mixing trusted and untrusted code, leaving the user to run potentially unsafe code without protections.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 6396
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore