Which of the BACnet IP Xdrivers is to be used for the CX9680?
  • Which of the BACnet IP Xdrivers is to be used for the CX9680?
  • BillNeville
    BillNeville
‎2018-09-06 12:24 PM
Confused about which file is for the CX9680
Xdriver
The two BACnet IP Xdriver files on the Extranet are called:
bacnetip120000.xdr
BacnetIP_bcx_122002.xdr
When loading the first one in a CX9680 the controller reset.
The file bacnetip120000.xdr is for first generation Continuum network controllers like the CX99xx, CX94xx, CX9201.
The file BacnetIP_bcx_122002.xdr is for the second generation controllers like the bCX9640, CX9680 (aka NC2) and the ACX57xx. It is NOT just for the bCX controller.