Some of the older access controllers do not support 2 card credentials for the personnel objects, which are these?
Cyberstation V1.90 and above
Access Controllers :
ACX700, 780
CX9900, CX9940
CX9702
ACX5740, 5720
Netcontroller II CX9680
Older controllers do not have the facility to support 2 credentials
  1. You require a minimum of Cyberstation V1.90 to support 2 Credentials in a personnel object, this is known as Transitional Card Support.
  2. The ONLY controllers that support dual cards are the ACX5740, ACX5720 and Netcontroller II (CX9680).