Where is graphic information stored in Continuum?
  • Where is graphic information stored in Continuum?
  • JohnBoehmer
    JohnBoehmer
  • AbeMeran
    AbeMeran
‎2018-09-06 10:06 AM
Last Updated: JohnBoehmer Schneider Alumni (Retired) ‎2020-02-12 09:49 AM
Where is graphic information stored in Continuum? Is any graphic information stored in the controller.
Andover Continuum
  • Continuum Cyberstation
  • Continuum webClient Server
Need to know where Continuum Graphic information is stored.
While during the Continuum installation process, pin files, image library files and background images are placed in the NewGraphicFiles folder on the workstation on which Cyberstation is installed, these files can alternately be stored on any network share.  Each workstation must have the location of these files defined in Pinpoint under View>Options.
The graphic information is stored in the dbo.Panel table in ContinuumDB.
The Graphics folder paths that are set from 'View\Options' are unique to each Cyberstation and are stored in the device table of the ContinuunmDB on the corresponding row of the appropriate Cyberstation in columns PPBackgroundsFolder, PPGraphicsFolder and  PPGraphicsLibraryFolder
No graphic information is stored in the controller