Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

When viewing the "Device Properties" of an MNB device in the Workplace Commissioning Tool (WPCT) the controller status indicates "Operational, Read-Only"?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • When viewing the "Device Properties" of an MNB device in the Workplace Commissioning Tool (WPCT) the controller status indica...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Kim_Baze
    Kim_Baze
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5401 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

When viewing the "Device Properties" of an MNB device in the Workplace Commissioning Tool (WPCT) the controller status indicates "Operational, Read-Only"?

Picard Product_Support
‎2018-09-06 10:52 AM

Last Updated: Administrator CraigEl Administrator ‎2023-09-12 08:22 PM

Issue

When viewing the "Device Properties" of an MNB device in the Workplace Commissioning Tool (WPCT) the controller status indicates "Operational, Read-Only"?

Product Line

TAC IA Series

Environment

  • BACnet MNB controllers
  • WorkPlace Commissioning Tool all versions

Cause

The MNB-xxxx series controllers contain circuitry that is designed to protect the integrity of the embedded flash memory under low-voltage or questionable input voltage conditions.  In the event of a controller-perceived low-voltage condition, the controller will set a read-only flag and lock out all writes to memory, as well as turn off controller outputs.

Resolution

The Read-Only status can help serve as an indicator that the input voltage to the controller may be questionable.

Attention should also be paid to the wire distance between the central transformer and the secondary loads, especially in the case of half-wave input devices like the MNB-70, MNB-V series and MNB-300 controllers and the MNB-1000-15 remote I/O module. With half-wave type input devices, significant AC input current spikes can occur during the positive half-cycle of the AC input. Large resistances due to the wire lengths can cause significant voltage drops as seen from the controller AC input. In extreme cases, the controller may enter the read-only mode at apparent AC voltages exceeding 20 Vac due to the asymmetrical nature of the AC input voltage waveforms. In these cases, reducing the load on the transformer, reducing the wire length between the controller and the transformer, and using higher current rated wire will correct the problem. 

For complete wiring guidelines consult the Micronet BACnet, Wiring, Networking, and Best Practices Guide.

Once the power issue is resolved cycling power to the controller will clear the read-only portion of the status. 

Labels (1)
Labels:
  • TAC IA Series
Attachments
Tags (2)
  • Find more articles tagged with:
  • 11869
  • CraigEllis23
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of