Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

When is a IA-BAC-500, IA-OPC-500, IA-SNMP-500 or IA-MOD-500 license option required?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • When is a IA-BAC-500, IA-OPC-500, IA-SNMP-500 or IA-MOD-500 license option required?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • JamesMorgan
    JamesMorgan
  • DavidFisher
    DavidFisher
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2255 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

When is a IA-BAC-500, IA-OPC-500, IA-SNMP-500 or IA-MOD-500 license option required?

Picard Product_Support
‎2018-09-06 12:22 PM

Last Updated: Lieutenant JG JamesMorgan Lieutenant JG ‎2023-12-18 11:19 AM

Issue

When is an "additional 500 points" license required for an Enterprise Server?

Product Line

TAC IA Series

Environment

I/A Series R2 IA-ENT-1 Enterprise Server licensed with the IA-DRV-OSD Open Systems Device driver license

Cause

The basic Enterprise Server license does not include any external point driver capabilities.   Adding the IA-DRV-OSD allows the enterprise server to communicate with up to 25 points of each type, BACnet, OPC, SNMP and ModBus, all using IP communications.

Resolution

An Enterprise Server can be licensed to directly communicate with  BACnet, OPC, MODbus and SNMP points by adding the IA-DRV-OSD license and will support communication with up to 25 points of each specific type of points.

For each additional block of 500 points of a specific type, you need to purchase an additional points license, IA-BAC-500, IA-OPC-500, IA-MOD-500 or IA-SNMP-500. 

Here is an example of how these licenses are used.  The Enterprise Server needs to communicate directly with 1250 BACnet IP points and 60 SNMP points. 

The following licenses will be required:

  • IA-ENT-1 -- Enterprise server license
  • IA-DRV-OSD -- Open System Driver for direct point communication, includes 25 points each of BACnet, SNMP, OPC and ModBus.
  • IA-SNMP-500 -- allows ES to communicate with the 60 SNMP points, technically allowing communications with a total of 525 SNMP points (25 points included with IA-ENT-1 and 500 with IA-SNMP-500).
  • IA-BAC-500 -- allows the ES to communicate with an additional 500 BACnet points bringing the total to 525 BACnet points
  • IA-BAC-500 -- this second IA-BAC-500 license will allow the ES to communicate with the additional 500 BACnet points, bringing the total allowable BACnet point count to 1025 points
  • IA-BAC-500 -- this third IA-BAC-500 license will allow the ES to communicate with the required additional 225 BACnet points, actually bringing the total allowable BACnet point count to 1525 points.

NOTE: On most computers an IA-ENT-1 with the Open System Driver is capable of supporting a maximum of 4000 external points regardless of the number of points licensed in any one communication type.

Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 7889
  • JamesMorgan23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore