Issue
When accessing an SNP network using TAC Vista, no values are displayed.
Product Line
Satchwell MicroNet, TAC VistaEnvironment
- Satchwell MicroNet
- TAC Vista
Cause
TAC Vista does not support LAN number 0. If the XBuilder-exported file assigns a LAN number of 0, TAC Vista will fail to display values from the SNP network.
Resolution
-
To resolve this issue:
-
Locate the XBuilder Exported File
- Find the
.XMLMfile generated by XBuilder.
- Find the
-
Edit the File
- Open the
.XMLMfile using a text editor such as Notepad.
- Open the
-
Modify the LAN Number
- Search for any instance where the LAN number is set to
0. - Change the LAN number from
0to1.
- Search for any instance where the LAN number is set to
-
Save the File
- Save the changes and reload the file in TAC Vista.
-
Verify
- Reconnect to the SNP network and confirm that values are now displayed correctly.
-