Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

What should be considered when analyzing the performance of a Modbus TCP/IP implementation?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What should be considered when analyzing the performance of a Modbus TCP/IP implementation?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa119747
    sesa119747
  • Alan_Wood
    Alan_Wood
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2242 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What should be considered when analyzing the performance of a Modbus TCP/IP implementation?

Picard Product_Support
‎2018-09-06 02:45 PM

Issue

What should be considered when analyzing the performance of a Modbus TCP/IP implementation?

Environment

Modbus TCP/IP implementation

Cause

Check the performance level of Modbus TCP/IP implementation for possible improvement.

Resolution

Determining if a Netcontroller will handle the load of a specific Modbus TCP/IP implementation must take into account many different factors. A lot depends upon the 3rd party device, the network utilization of the IP network, the number of devices/points being polled and the speed/polling rate of the devices on the RS485 network. The Modbus TCP/IP xdriver behaves as a client and polls for information in a round robin basis. The more data it has to poll the longer it will take.

The organization of the Modbus Addresses is also important.

For example:

  1. If 12 registers are at consecutive address locations i.e. 11, 12, 13, 14, 15, 16, 17, 18, 19, 20, 21, 22, then 1 data packet is required to retrieve all this information.
  2. If only a few registers are at consecutive locations i.e. 1, 2, 3, 8, 21, 22, 23, 30, 40, 65, 66, 67 then 6 data packets are required to retrieve this information.
  3. If the registers are all in separate locations i.e. 1, 5, 10, 20, 30, 40, 50, 60, 70, 80 then 10 data packets, one for each address is required.

The third example would take 10 times longer than the 1st to poll the address information. If address locations in the 3rd party device cannot be altered then it may be more efficient to create additional xdriver points to effectively 'fill the gaps' so as to reduce the number of data packets.

It is recommended to carry out a bench test with the devices in order to analyze the configuration. This would allow for adjustments of the requests or adding additional hardware to poll the amount of required information.

Field Example:
Using a Modbus TCP/IP xdriver to poll a number of Powerlogic metering devices. Considering 30 EGX's/ECC's involved, plus two Powerlink 3000 panels, using 33 IP addresses. Each EGX/ECC has from 10-20 Modbus devices attached on the RS485 side. Each metering device will be polled for about 12 registers. In this example, we would be polling about 4000-5000 register points via Modbus TCP/IP with a NetController2.

In this particular scenario, it was determined that 2 Netcontroller IIs would be needed to handle the amount of polling required at the expected performance level.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 3125
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.