Issue
What is the switching level resistance for a digital input to be seen as 1 in a Xenta 411/412 I/O modules
Environment
Xenta 411/12
Cause
Integrating third party devices with Xenta 411/412 I/O modules.
Resolution
The switching level resistance for a digital input to be seen as 1 in a Xenta 411/12 is around 2000ohm