What is the replacement for a Drayton Theta YBL3 Valve Body / Actuator assembly?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What is the replacement for a Drayton Theta YBL3 Valve Body / Actuator assembly?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
11693 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What is the replacement for a Drayton Theta YBL3 Valve Body / Actuator assembly?

Picard Product_Support
‎2018-09-10 03:02 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 06:27 PM

Issue

The Drayton Theta YBL3 Valve Body / Actuator assembly is to be replaced.

Environment

  • Replacement
  • Drayton
  • Actuator
  • Valve
  • YBL3

Cause

The Drayton Theta YBL3 Valve Body / Actuator assembly is obsolete.

Resolution

OVERVIEW

The Drayton Theta YBL3 Valve Body / Actuator assembly is obsolete, and there is no purpose built replacement.

The Valve Body was available in 1.1/4", 1.1/2" and 2" B.S.P. sizes and was normally installed as a mixing valve in variable temperature, constant volume, compensated heating circuits.

No Valve Body / Actuator assemblies are currently available in these sizes.

Details of the YB Valve Body may be viewed here.

 

VALVE BODY REPLACEMENT

To replace the YBL3 Valve Body the following is required:-

S-E Satchwell MB Valve Body of appropriate size - MB1552 (1.1/4"), MB1602 (1.1/2"), MB1652 (2")

Details of the MB Valve Body may be viewed here.

 

ACTUATOR REPLACEMENT (6-WIRE INSTALLATION)

The YBL3 Actuator normally comprised a 6-wire electrical connection enabling it to be operated by a Theta Potentiometric Controller as follows :- 

Terminal M1 – Open signal

Terminal M2 – Close signal

Terminal M3 – Common 

Terminal M4 – 135 ohm Feedback Potentiometer – winding

Terminal M5 – 135 ohm Feedback Potentiometer – wiper

Terminal M6 – 135 ohm Feedback Potentiometer – winding

Where 6 wires are connected to the YBL3 Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :-

MD10B-24

MD20B-24 (if MD10B-24 not available)

Details of the MD10B-24 Actuator may be viewed here

Details of the MD20B-24 Actuator may be viewed here.

N.B.

The YBL3 Actuator may also have included an additional 2-wire electrical connection associated with integral Transfer Switches wired as follows :- 

Terminal M7 – M1 made to M7 when YBL3 Fully Closed (24Vac)

Terminal M8 – M2 made to M8 when YBL3 Fully Open (24Vac)

Where external wiring is connected to YBL3 Transfer Switch Terminals M7 or M8 then an Auxiliary Switch Kit containing two S.P.C.O. Auxiliary Switches should be installed on the MD Actuator.

Auxiliary Switch Kit MD-S2 (914-1061-000)

Details of the MD-S2 Auxiliary Switch Kit may be viewed here.

Where external wiring is connected to YBL3 Terminal M7 then the MD-S2 Auxiliary Switch Kit should be wired as follows :-

Terminal S1 (Common) - connect to 24Vac power source

Terminal S2 (Normally Closed) - connect to 24Vac device previously connected to YBL3 Terminal M7

Terminal S3 (Normally Open) - no connection necessary

Where external wiring is connected to YBL3 Terminal M8 then the MD-S2 Auxiliary Switch Kit should be wired as follows :-

Terminal S4 (Common) - connect to independent 24Vac supply

Terminal S5 (Normally Closed) - no connection necessary

Terminal S6 (Normally Open) - connect to 24Vac device previously connected to YBL3 Terminal M8

 

LINKAGE KIT

A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body.

Linkage Kit LMD/AR-MB (914-1071-000)

Details of the LMD/AR-MB Linkage Kit may be viewed here

 

IMPORTANT NOTE

In such 6-wire installations not only will the YBL3 Valve / Actuator assembly need to be replaced but the associated Theta Potentiometric Controller and its Sensors will also need to be replaced.

 

CONTROLLER REPLACEMENT

The Theta Potentiometric Controller may be replaced by the S-E Satchwell CSC5252 or the CSC5352 Compensator Controller.

Details of the CSC Controllers may be viewed here.

 

SENSOR REPLACEMENT

Theta 3-wire Temperature Sensors may be replaced by S-E Satchwell 2-wire Temperature Sensors compatible with the S-E Satchwell CSC 5252 or CSC5352 Compensator Controllers selected from the following as appropriate.

Outside Air Temperature Sensor (STO 600)

Contact Temperature Sensor (STC 600), or alternatively :-

Immersion Temperature Sensor (STP 660) + Sensor Pocket Adaptor (DWA 0001)

Room Temperature Sensor (STR 600) – OPTIONAL ONLY

Details of the STO 600 Outside Air Temperature Sensor may be viewed here

Details of the STC 600 Contact Temperature Sensor may be viewed here.

Details of the STP 660 Water Temperature Sensor may be viewed here.

Details of the DWA 0001 Sensor Pocket Adaptor may be viewed here.

Details of the STR 600 Room Temperature Sensor may be viewed here.

 

ACTUATOR REPLACEMENT (3-WIRE INSTALLATION)

Should only 3 wires be connected to a YBL3 Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :-

MD10B-24

MD20B-24 (if MD10B-24 not available)

Details of the MD10B-24 Actuator may be viewed here.

Details of the MD20B-24 Actuator may be viewed here.

N.B.

The YBL3 Actuator may also have included an additional 2-wire electrical connection associated with integral Transfer Switches wired as follows :- 

Terminal M7 – M1 made to M7 when YBL3 Fully Closed (24Vac)

Terminal M8 – M2 made to M8 when YBL3 Fully Open (24Vac)

Where external wiring is connected to YBL3 Transfer Switch Terminals M7 or M8 then an Auxiliary Switch Kit containing two S.P.C.O. Auxiliary Switches should be installed on the MD Actuator.

Auxiliary Switch Kit MD-S2 (914-1061-000)

Details of the MD-S2 Auxiliary Switch Kit may be viewed here

Where external wiring is connected to YBL3 Terminal M7 then the MD-S2 Auxiliary Switch Kit should be wired as follows :-

Terminal S1 (Common) - connect to 24Vac power source

Terminal S2 (Normally Closed) - connect to 24Vac device previously connected to YBL3 Terminal M7

Terminal S3 (Normally Open) - no connection necessary

Where external wiring is connected to YBL3 Terminal M8 then the MD-S2 Auxiliary Switch Kit should be wired as follows :-

Terminal S4 (Common) - connect to independent 24Vac supply

Terminal S5 (Normally Closed) - no connection necessary

Terminal S6 (Normally Open) - connect to 24Vac device previously connected to YBL3 Terminal M8

 

LINKAGE KIT

A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body.

Linkage Kit LMD/AR-MB (914-1071-000)

Details of the LMD/AR-MB Linkage Kit may be viewed here

In such 3-wire installations the YBL3 Valve / Actuator assembly only will need to be replaced, while any associated Controller and Sensors may be retained.

Labels (1)
Labels:
  • Field Devices
Attachments
Tags (1)
  • Find more articles tagged with:
  • 6211
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore