What is the replacement for a Drayton Theta YBL1A Valve Body / Actuator assembly?
  • What is the replacement for a Drayton Theta YBL1A Valve Body / Actuator assembly?
  • CraigEl
    CraigEl
‎2018-09-10 12:17 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-14 06:45 PM
The Drayton Theta YBL1A Valve Body / Actuator assembly is to be replaced.
Field Devices
  • Replacement
  • Drayton
  • Actuator
  • Valve
  • YBL1A
The Drayton Theta YBL1A Valve Body / Actuator assembly is obsolete.
OVERVIEW
The Drayton Theta YBL1A Valve Body / Actuator assembly is obsolete, and there is no purpose built replacement.
The Valve Body was available in 1.1/4", 1.1/2" and 2" B.S.P. sizes and was normally installed as a mixing valve in variable temperature, constant volume, compensated heating circuits.
No Valve Body / Actuator assemblies are currently available in these sizes.
Details of the YB Valve Body may be viewed here.
VALVE BODY REPLACEMENT
To replace the YBL1A Valve Body the following is required:-
S-E SatchwellMB Valve Body of appropriate size - MB1552 (1.1/4"), MB1602 (1.1/2"), MB1652 (2")
Details of the MB Valve Body may be viewed here.
ACTUATOR REPLACEMENT (6-WIRE INSTALLATION)
The YBL1A Actuator normally comprised a 6-wire electrical connection enabling it to be operated by a Theta Potentiometric Controller as follows :-
Terminal M1 – Open signal
Terminal M2 – Close signal
Terminal M3 – Common
Terminal M4 – 135 ohm Feedback Potentiometer – winding
Terminal M5 – 135 ohm Feedback Potentiometer – wiper
Terminal M6 – 135 ohm Feedback Potentiometer – winding
Where 6 wires are connected to the YBL1A Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :-
MD10B-24
MD20B-24 (if MD10B-24 not available)
Details of the MD10B-24 Actuator may be viewed here
Details of the MD20B-24 Actuator may be viewed here.
N.B.
The YBL1A Actuator also included an additional 3-wire electrical connection associated with an integral S.P.C.O. Auxiliary Switch wired as follows :-
Terminal S1 – Normally Closed Contact
Terminal S2 – Common
Terminal S3 – Normally Open Contact
Where external wiring is connected to the YBL1A Actuator Auxiliary Switch then an Auxiliary Switch Kit containing a S.P.C.O. Auxiliary Switch should be installed on the MD Actuator.
Auxiliary Switch Kit MD-S1 (914-1060-000)
Details of the MD-S1 Auxiliary Switch Kit may be viewed here.
The MD-S1 Auxiliary Switch Kit should be wired as follows :-.
Terminal S1 – Common
Terminal S2 – Normally Closed Contact
LINKAGE KIT
A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body.
Linkage Kit LMD/AR-MB (914-1071-000)
Details of the LMD/AR-MB Linkage Kit may be viewed here
IMPORTANT NOTE
In such 6-wire installations not only will the YBL1A Valve / Actuator assembly need to be replaced but the associated Theta Potentiometric Controller and its Sensors will also need to be replaced.
CONTROLLER REPLACEMENT
The Theta Potentiometric Controller may be replaced by the S-E Satchwell CSC5252 or the CSC5352 Compensator Controller.
Details of the CSC Controllers may be viewed here.
SENSOR REPLACEMENT
Theta 3-wire Temperature Sensors may be replaced by S-E Satchwell 2-wire Temperature Sensors compatible with the S-E Satchwell CSC 5252 or CSC5352 Compensator Controllers selected from the following as appropriate.
Outside Air Temperature Sensor (STO 600)
Contact Temperature Sensor (STC 600), or alternatively :-
Immersion Temperature Sensor (STP 660) + Sensor Pocket Adaptor (DWA 0001)
Room Temperature Sensor (STR 600) – OPTIONAL ONLY
Details of the STO 600 Outside Air Temperature Sensor may be viewed here.
Details of the STC 600 Contact Temperature Sensor may be viewed here.
Details of the STP 660 Water Temperature Sensor may be viewed here.
Details of the DWA 0001 Sensor Pocket Adaptor may be viewed here.
Details of the STR 600 Room Temperature Sensor may be viewed here.
N.B.
ACTUATOR REPLACEMENT (3-WIRE INSTALLATION)
Should only 3 wires be connected to a YBL1A Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :-
MD10B-24
Details of the MD10B-24 Actuator may be viewed here.
N.B.
LINKAGE KIT
In such 3-wire installations the YBL1A Valve / Actuator assembly only will need to be replaced, while any associated Controller and Sensors may be retained.
  • Field Devices
  • 5448