Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

What is the recommended method to upgrade a Niagara R2 station to a newer version?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What is the recommended method to upgrade a Niagara R2 station to a newer version?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • sesa116877
    sesa116877

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
4427 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What is the recommended method to upgrade a Niagara R2 station to a newer version?

Picard Product_Support
‎2018-09-07 03:35 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-11-04 09:02 AM

Issue

What is the recommended method to upgrade a Niagara R2 station to a newer version?

Product Line

TAC IA Series

Environment

I/A Series Niagara R2

Cause

Unsure how to upgrade station databases.

Resolution

The published upgrade procedure is provided in F-27334. Below is a modified method that also works. Doing station upgrades on the server first is preferred. If there are any errors, they can be addressed without operational interruptions.

  1. Using the existing version of WorkPlace Pro (WPP), backup ALL of the UNC and Server databases into XML format.
    • Methods of backing up and converting databases.
      • Open the Enterprise server in WorkPlace Pro. Double click the station name. Select "Commands" and "Backup XML to save the server in XML. Then select "Backup Subordinate XML" to pull all of the UNC databases as XML into the server stations folder.
        backupXml.gif

         

      • If not on site but the UNC and Server databases are available, use the DB Admin tab of the Admin tool to convert the databases locally to XML.
  2. Now install the newer Niagara revision onto the Server.
  3. Copy the stations containing the XML files to the desired WPP revision station folder.
  4. Enable and open the new revision of WPP.
  5. Use the Admin Tool to convert locally all of the stations from XML to DB. (If there are any errors, they can be addressed without affecting the running installation.)
  6. After all the databases have successfully converted to DB, convert them to SNS. (This saves time later if the UNCs need reloading)
  7. Use the Enterprise Server to upgrade the UNC. During the upgrade process of the UNC it will ask to backup the database. If the database had upgraded with no issue in the previous step, enter the username and password to proceed with this backup. This will backup the station, upgrade the UNC, and then upgrade and reinstall the station. The previous station upgrade will be needed only if there is an issue.

If after following this procedure the station still fails to start, contact Product Support Services.

Labels (1)
Labels:
  • TAC IA Series
Attachments
Tags (1)
  • Find more articles tagged with:
  • 3849
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore