Issue
What is the minimum pulse duration for the digital inputs (X1 - X3) on the TAC Xenta 121-FC?
Product Line
TAC VistaEnvironment
- Vista Server
- Xenta 121
Cause
The device requires a certain pulse duration to be able to register the feedback signal from another device, such as a fan running signal.
Resolution
The minimum pulse input duration is 250ms.
Click here to open the datasheet for Xenta 121-FC