What is the limit to the number of objects that can be created in a Workstation?
  • What is the limit to the number of objects that can be created in a Workstation?
  • DavidChild
    DavidChild
  • Dave_Shore
    Dave_Shore
  • AdamSteele
    AdamSteele
‎2018-09-06 09:58 AM
Last Updated: Sisko DavidChild Sisko ‎2021-09-27 02:12 AM
Andover Continuum
CyberStation
Want to create a large number of AnalogValue's and BinaryValues in the Workstation for programming and display purposes.
There are no limits to the number of variable objects that can be created in the Workstation. There may well be some practical limits based on the SQL limitations but for all intents and  purposes this limit will most likely not be reached on a full SQL install. There maybe issues with DB size on an SQL Express system but even then, the AV / BV objects don't actually take up that much physical space.
As an example, tested this on a v1.94 system and have been able to create over 2500 AV's in my Workstation folder without any issues.
NOTE - Running a large number of Programs on a CyberStation can cause issue. System control, etc. should be from a Controller rather than CyberStation.
Tags (2)
  • 14668
  • DavidShore21