Confusion in documentation of the output type of an STR300 temperatire transmitter
Field Devices
STR300 series transmitter
The STR300 is an electronic living space transmitter that converts a measured temperature into an electric current signal. The transmitter is delivered as a complete unit, comprising a Pt100 classB sensing element and an amplifier mounted in a housing. STR300 is intended either for surface mounting on a wall or installation in a standard switch box in dry, dust free rooms.
The HVAC Sensors Catalogue incorrectly shows that the STR300 Series has an Output of 0-10V while  the datasheet correctly shows the output as 4-20ma.
The STR300 has an output signal of 4 to 20 mA corresponding to a temperature range of 0-40°C