What is the BACnet MSTP unit load of the SpaceLogic SP90 PIBCV actuators

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What is the BACnet MSTP unit load of the SpaceLogic SP90 PIBCV actuators
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
1373 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What is the BACnet MSTP unit load of the SpaceLogic SP90 PIBCV actuators

Administrator CraigEl Administrator
‎2021-10-04 03:44 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:26 AM

Issue

What is the unit load (UL) of the SpaceLogic SP90 PIBCV Actuators that will help me to calculate how many SP90 PIBCV Actuators can be added on ComA and ComB of a SmartX Server.

Product Line

EcoStruxure Building Operation, Field Devices

Environment

  • SpaceLogic SP90 PIBCV Actuator
  • SmartX Server

Cause

Require the Unit Load (UL) of the SpaceLogic SP90 PIBCV Actuator to calculate the number of actuators allowed on the RS-485 network. 

Resolution

The Generic application note AN01 can be applied with answers to the transceiver interface attributes below. The SpaceLogic SP90 PIBCV Actuator range uses the SN65HVD1780DR transceivers which are a failsafe transceiver (not requiring bias) and reduced 1/10 UL. In addition, there are no local bias resistors and therefore the 1/10 UL of the transceiver would be the total UL presented to the bus by the SpaceLogic SLP Room Unit.

Transceiver Xcvr Unit Load Xcvr Failsafe Adaptor Circuit Bias Circuit Bias Load Total Unit Load Isolated 485 Bus
SN65HVD1780DR 0.1 Yes None None 0.1 No


Based on the above the total number of devices can be calculated as 32/0.1 = 320.

The BACnet MSTP standard specifies that the address range for BACnet master devices is 0-127 and therefore a SmartX Server is limited to 127 devices per com port (254 total per Server) so this should effectively be the limiting factor. However, the documentation recommends using only up to 64 devices with the same RS-485 transceiver, or 32 devices with different RS-485 transceivers.

 

Since the SpaceLogic SP90 PIBCV Actuator does not have an isolated RS-485 interface it conforms to Generic RS-485 Network Device Configuration 1 in EBO Webhelp.  A network consisting of only SpaceLogic SP90 PIBCV Actuators should only require a 120-ohm termination resistor at each end of the bus and not require any bias resistors.

Also, check out the SmartStruxure-RS485-Controller Unit Load Quick-Help video on the Exchange.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • CraigEllis21
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore