What functionality do the AC-1 modules provide when the Netcontroller goes offline?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What functionality do the AC-1 modules provide when the Netcontroller goes offline?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • GavinHe
    GavinHe
  • PaulFr
    PaulFr
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2379 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What functionality do the AC-1 modules provide when the Netcontroller goes offline?

Picard Product_Support
‎2018-09-07 07:27 AM

Last Updated: Sisko GavinHe Sisko ‎2023-04-17 01:29 AM

Issue

When a Netcontroller is powered off, resets or loses communication to the AC-1 IOU modules, the modules become stand alone.

Product Line

Andover Continuum

Environment

  • Netcontroller II (CX9680), Netcontroller (CX9900, CX9940)
  • IOU Modules AC-1, AC-1A, AC-1Plus
  • Custom Wiegand
  • Events

Cause

Need to understand what functionality AC-1 IOU modules provide without a Netcontroller

Resolution

If using one of the standard Wiegand data formats i.e. Continuum 37 bit, 26 bit etc then the AC-1 module will operate in site code only:

  • This is known as degrade mode and means any card from that site will be granted access to the door.
  • The module verifies the presented card is of the correct data format and has the correct parity,
  • The module checks the site code against one of the 4 possible site codes stored in NVRAM.
  • The AC1 and AC-1A only support the first two site codes in degrade mode.

  • The AC-1Plus can support all four site codes in degrade mode.

  • There is no recording of events when the Netcontroller comms are lost.

  • Programs that are controlling the module no longer work

This is different to normal operation where both the card number and the site code are verified to ensure that the individual person has access to the specific area.

 

When using custom card formats and the module is operating in degrade mode:

  • Refer to Setting Up a Custom Wiegand Format for information on the behavior of the AC-1, AC1-A and AC1Plus.
  • Refer to Multi Custom Card Formats as the site codes also need to be saved in the AC1 module using a Plain English program, 
Labels (1)
Labels:
  • Andover Continuum
Attachments
Tags (2)
  • Find more articles tagged with:
  • 4661
  • GavinHeward23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore