Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

What does the Error LED on a NetController/CX9900 indicate.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What does the Error LED on a NetController/CX9900 indicate.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • JohnBoehmer
    JohnBoehmer
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2624 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What does the Error LED on a NetController/CX9900 indicate.

Picard Product_Support
‎2018-09-06 01:05 PM

Issue

 The error LED on a CX9900 Controller is flashing.  What does this mean.

What do the various NetController Error LED blink rates indicate.

Environment

  • NCI
  • CX9900
  • CX9000

Cause

An controller error has occurred.

Resolution

The ERROR indicator remains OFF until an error occurs.

If the NetController fails an internal system test, the ERROR indicator blinks a preset number of times, then pauses, and repeats the blinking and pausing sequence. This blinking pattern will persist until you reset the controller.

The number of blinks between pauses identifies the specific problem (as shown in the table below).

ERROR Indicator Blink Rates (before a pause)

# Blinks                Type of Failure                                                              

17                           CX Firmware is corrupt (Bad Flash/ROM or bad update)

18                           LAN Card's memory is faulty - Try replacing the LAN Card.

19                           Problem creating certain System Tasks - Maybe due to lack of memory.

20                           Problem with the NIC - Try replacing the LAN Card

22                           RTC Failed - Possible Hardware issue

24                           Problem with the PIT chip - H/W related

25                           Problem creating Timer Tasks - Maybe due to lack of memory

28                           The RAM memory is faulty or bad. Try replacing the RAM module(s).

29 to 62                                 Problem creating certain System Tasks - Maybe due to lack of memory.

63                           Copy protection - Flash Upgrade file is invalid for this Controller

(UPD file is Serial # protected)

64                           Problem creating the Uprev task - Maybe due to lack of memory.

Note: If a Plain English program disables due to an error, the ERROR indicator illuminates and stays ON (without blinking)—if this occurs, you can turn the indicator off by setting the ERRORS system variable to zero.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 6579
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore