Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

What controller ports and physical standards are supported by the Modbus X Drivers?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What controller ports and physical standards are supported by the Modbus X Drivers?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4546 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What controller ports and physical standards are supported by the Modbus X Drivers?

Product_Support
‎2020-09-01 06:49 AM

Last Updated: ContentModerator Explorer ‎2025-08-11 04:09 AM

Issue

When using the Modbus RTU and Modbus IP XDrivers it is important to determine which controller and port can support the electrical standards used by the 3rd party device.

Product Line

Andover Continuum

Environment

  • Continuum Netcontroller II and bCX1 controllers that have been XDriver enabled.
  • XDriver, Modbus RTU, IP, Infilink, Infilink200, B-Link. RS-232, RS-485
  • JBUS

Cause

Controller ports and 3rd party devices come in various electrical standards (RS-232, RS-485, RS-422), which ports support the various standards?

Resolution

There are two Continuum Modbus XDrivers:

Modbus RTU: This allows the connection of 3rd party Modbus RTU slaves via the serial data RS-232, RS-485 or RS-422 electrical standards. RS-232 is a point to point connection to 1 device, RS-485 & RS-422 support a bus topology for connection of multiple 3rd party devices.

The Continuum controller will be the Modbus RTU Master and will poll the 3rd party device that must be a slave.

The bCX1-CR controllers have 2 ports that can be configured for Modbus:

Comm1 RS-232

Comm2 RS-232 or RS-485 port

The Netcontroller II controllers support:

Comm1 - RS-232 or RS-485

Comm2 - RS-485

Comm3 - RS-232

Comm4 - RS-422

The ACX57xx controllers support:

Comm1 - RS-485

Notes
An Infilink200 or B-Link may be used to convert RS-232 to RS-485 if required.
The J Bus protocol is a subset of the Modbus protocol and so the Modbus XDriver is used for J Bus Systems.

Modbus IP: The bCX1, ACX57xx and the Netcontroller II all support the Modbus IP protocol that connect via the Ethernet IP connection. This XDriver can be configured to support either Client or Server modes. Although the communication is physically via the Ethernet port, one of the Serial ports is required to be X Driver enabled to load the software, this serial port is then no longer available for other purposes.

This XDriver requires Ethernet X Driver support to be enabled on the port.

NOTE Netcontroller II and bCX1 can have an XDriver ENABLED on more than a one Comms port, however only one IP XDriver should be INSTALLED on each controller, also only one Modbus RTU XDriver should be INSTALLED on each controller. It is possible to INSTALL a Modbus RTU and a Modbus TCP/IP XDriver on a single controller, but it would be very easy to overload the controller, so this setup is only suitable for smaller networks. (note the difference between enabling XDriver support and Installing an XDriver)

See Articles Can multiple Modbus TCP/IP XDrivers be installed on a single 2nd Generation NetController? and BCX Controller can use Comm 1, Comm2, or both ports for Modbus RTU X-Driver

 

Labels (1)
Labels:
  • Andover Continuum
Tags (5)
  • Find more articles tagged with:
  • 4234
  • acx
  • b-link
  • bcx
  • blink
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore