Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

BCX Controller can use Comm 1, Comm2, or both ports for Modbus RTU X-Driver

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BCX Controller can use Comm 1, Comm2, or both ports for Modbus RTU X-Driver
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa119747
    sesa119747
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2955 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BCX Controller can use Comm 1, Comm2, or both ports for Modbus RTU X-Driver

Picard Product_Support
‎2018-09-06 02:38 PM

Issue

With the BCX Controller you can use either the Comm 1 or Comm2 port for the Modbus RTU X-Driver or you could use both simultaneously.

Product Line

Andover Continuum

Environment

  • BCX Controller
  • Modbus RTU X-Driver

Cause

Enable Comm port for X-Driver

Resolution

Use either Comm port for the Modbus RTU X-Driver as per page 16 of the Modbus RTU user guide.

If you use Comm2 you forfeit the Infinet or MSTP port, you must also create the Communications Configuration Point (Function 99) to tell the X-Driver if it should use RS232 or RS485 on Comm2.

This point is required because on the BCX Comm 2 the X-Driver needs to tell the BCX to use the RS485 port (if that is what you want to use) not the RS232 port it defaults to in its Operating System. If you did not create the point the driver would default to the RS232 port.

RS485 is half duplex so when transmitting data out the RS485 port, the driver needs to turn off the receiver so that it does not receive its own transmission. Also normally RS232 is full duplex and does not have to do this.

However be aware that on BCX's Comm2 both the RS232 and RS485 ports are Half duplex, which although does not normally cause issues with Modbus because it is a Master / Slave network where we never get unsolicited data, it could cause an issue on other protocols.

You can have X-Driver enabled on either or both ports, and there is nothing to stop you from having 2 Modbus networks, one on Comm1 the other on Comm2. You could even use a RS232 to RS485 converter on Comm1 if necessary (An Infilink200 would work fine). NOTE: The ability to enable 2 comm ports using Xdrivers can be done, but is not recommended by the Xdriver developers nor supported by PSS.

The RTU Xdriver is poll on demand. This type of driver can request a lot of data and starve the CPU on the controller which then makes the polling irregular. If 2 ports are being used then there are typically more devices being added and therefore more points increasing the requests and demand on the controller's CPU.

Use one program to control the polling on both ports. Two programs attempting to control the polling asynchronously will cause communication issues.

The BCX is able to run 2 X-Drivers but will be a little slower than having 2 BCX's. It is really down to the individual project. If it has big networks connected or update speed is critical then split across 2 controllers. If you just have a few devices on each port and the update time is not critical then you would be fine with 1 controller.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 3423
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of