Issue
What are the valid Electrical Types for the smart sensor input on a controller
Product Line
Andover Continuum, EcoStruxure Building Operation
Environment
- BACnet b3 controllers
- Infinet i2 controllers
- Smart or Room Sensor Input
- b3/i2 controllers excluding b3/i2 608, 824 and 885V
Cause
What are the valid Electrical Types for the smart input on a controller?
Resolution
Input X (SmartSensor) valid Electrical Types are:-
ACC_TEMP_DEGF
ACC_TEMP_DEGC
Digital
Note
If using a Smart sensor then ACC_TEMP_DEGF or ACC_TEMP_DEGC should be used
The temperature range is limited, thus room sensors can be used but not duct or pipe sensors as the temperature range is limited to 0-50DegC