What are the valid Electrical Types for the smart sensor input on a controller
  • What are the valid Electrical Types for the smart sensor input on a controller
  • CraigEl
    CraigEl
  • Dave_Shore
    Dave_Shore
‎2018-09-06 12:08 PM
Last Updated: Administrator CraigEl Administrator ‎2022-08-31 09:46 PM
Andover Continuum, EcoStruxure Building Operation
  • BACnet b3 controllers
  • Infinet i2 controllers
  • Smart or Room Sensor Input
  • b3/i2 controllers excluding b3/i2 608, 824 and 885V
What are the valid Electrical Types for the smart input on a controller?
Input X (SmartSensor) valid Electrical Types are:-
ACC_TEMP_DEGF
ACC_TEMP_DEGC
Digital
Note
If using a Smart sensor then ACC_TEMP_DEGF or ACC_TEMP_DEGC should be used
The temperature range is limited, thus room sensors can be used but not duct or pipe sensors as the temperature range is limited to 0-50DegC