What are the sensor temperature vs resistance values of the TC range of thermostats.
  • What are the sensor temperature vs resistance values of the TC range of thermostats.
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • Gary
    Gary
‎2018-09-11 07:51 AM
Last Updated: Administrator CraigEl Administrator ‎2023-06-08 12:06 AM
Resistance against temperature
Field Devices
  • TC300 thermostat range
  • TC900 thermostat range
  • RS-03 remote sensor
Remote sensor compatibility
The TC thermostat range use a 10K type 3 (3950) Negative Temperature Coefficient (NTC) thermistor. Whilst this is similar to the 10K type 3 thermistor used in the other BMS field device sensors such as the SpaceLogic SLA range, it has a different resistance curve and the temperature read will be different.
The table below shows that at typical room temperatures the error is 0.6°C or less.
T(°C) RS-03 R(KΩ) SPA R(KΩ) Error % Error °C
0 31.77 29.575 6.91% 1.736
5 24.94 23.504 5.76% 1.366
10 19.68 18.809 4.43% 1.052
15 15.62 15.146 3.03% 0.812
20 12.47 12.271 1.60% 0.63
25 10 10 0.00% 0
30 8.064 8.195 -1.62% 0.3872
35 6.538 6.752 -3.27% 0.3052
40 5.327 5.592 -4.97% 0.2422
45 4.363 4.655 -6.69% 0.1928
50 3.592 3.893 -8.38% 0.1542
Click here to view the TC thermostat's RS-03 remote temperature against resistance chart.
Click here to download the chart that provides the temperature against resistance reading for the TC thermostat's RS-03 remote temperature sensors.
  • Field Devices
NTC10K (3950) chart.zip
Tags (2)
  • 16246
  • CraigEllis23