Decoding information from the door's DoorFault attribute value.
Andover Continuum
  • CyberStation
  • CX9702
  • CX9680
  • ACX5740
  • ACX5720
  • ACX701
  • ACX781
The door's DoorFault attribute value is a weighted bit map that encodes information about a problem with the door as a whole or with one or both sides of a single reader/dual reader door.
The attribute is a bitmap that contains the following data:
Door Fault Codes
BIT VALUE DESCRIPTION
1 1 ACX Database Fault
2 2 Entry Keypad Tamper
3 4 Exit Keypad Tamper
4 8 Entry Reader Bit Fault
5 16 Exit Reader Bit Fault
6 32 Bond Sensor Violation
7 64 Unused
8 128 Unused
For example, a value of 2 indicates a keypad tamper at the entry reader, a value of 4 is a keypad tamper at the exit reader, 6 is keypad tamper at both readers and so on.
Note: The AlarmEnrollment Alarmed Attribute has a dropdown box that includes Doorfault. Ignore that. Set The AlarmEnrollment Alarmed Attribute to be Value and the Expression to be DoorFault = 2 in order to alarm a keypad tamper at the entry reader.