Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

What are the locations where Controller configuration data is saved?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What are the locations where Controller configuration data is saved?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • AdamSteele
    AdamSteele
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2251 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What are the locations where Controller configuration data is saved?

Picard Product_Support
‎2018-09-06 11:33 AM

Issue

What are the locations where Controller configuration data is saved?

Environment

Continuum Cyberstation

Continuum Controllers

Cause

Unsure as to where controller configuration information is stored and how to clear/reset this information if required.

Resolution

There are a number of different locations that a controllers database (configuration information) is stored - there are four locations for a BACnet controllers database and three for an Infinity controller.


1. Continuum SQL Database - Infinet tree


In Continuum Explorer, this is where the controller is originally created as a Device object under a Network Folder and commissioned into the Database. This is the location where objects (inputs, outputs, programs, etc...) are created. When creating a new object, it is created in both the SQL Database and also sent out to the controllers database at the same time.

The controllers information stored in the SQL Database can be sent out to the controller at any time by performing a reload of that controller (right-click Device object, Send to controller).

This information can be removed from the database and the controller by deleting individual objects or by deleting the entire Device object. If the Workstation where this delete was performed is online to the field devices then the same object(s) will be removed from the live controller in the field as well as from the SQL Database. If the Workstation is offline to the field controllers  (Workstations can be taken offline for offline editing) then this delete is only applied to the objects in the SQL Database – the objects will still be located in the controllers though, creating a mismatch between the two until the controller is reloaded.

2. Controller RAM

This is the active location of memory on the controller where the running database resides. On most controllers there is a backup battery that keeps this RAM alive with a trickle current when there is no power to the controller. When the controller is powered up it first tries to load its active database from RAM - this is the most current backup.

The database in controller RAM can be cleared by pressing the Reset button on the Runtime tab of the controllers Device object in Continuum Explorer.

3. Controller FLASH

This is the backup location of where the controllers configuration database resides. At any time the active RAM database can be saved to backup Flash by selecting "save to flash" from the controllers Device object in Continuum Explorer. This then makes an exact copy of the database in RAM (excluding point values) that can be restored at a later date either manually or automatically if the controller reboots and their is no valid database in RAM.

For Netcontrollers and bCX's, this database saved to Flash can be deleted from the controllers configuration page (configuration webpage) select Clear Database Backup and then commit changes to controller. If the controllers webpage cannot be accessed, pushing and holding down the controller's reset IP switch for 30 seconds clears any backup in flash in addition to resetting the IP address and ACC node id to default.

Another way to clear a controllers flash is to save a blank controller database to flash. Create a new controller Device object and then save that to flash.

4. Continuum SQL Database - BACnet tree

The information stored in the BACnet tree is the BACnet side of our configured Infinet objects. This is the BACnet objects as seen in the controller and as third-party BACnet Devices will see them.

When performing a "send to database" on the BACnet side, the Workstation goes out to the controller in the field, grabs all the BACnet objects and exposes them in the BACnet tree so that they can be used within Continuum.

These can be deleted from the BACnet tree without harming those objects configuration in the controller or the Infinet tree.

To recap:

 

To Create and save objects to the controller requires a two step process.

  • Step 1: Create Database objects using Continuum Cyberstation. Objects are added to both the active RAM of the Controller and the SQL Database.
  • Step 2: Save to Flash on the Controller. The objects in active RAM are backed up to the Flash RAM.

If unsure, the only way to know that the Database in the RAM and Flash is the same as that in the SQL Database is to perform a reload of the Controller and then backup to Flash.

  • Step 3: Send to Controller to reload configuration information from SQL Database to Controller RAM. After reload, redo Step 2 to backup to Flash.


To completely wipe configuration information from a controller in the field you will need to clear its active RAM and its backed up Flash. If you want to clear all information of the controller from the field and the SQL Database then you will need to clear the RAM and Flash and delete the Device object from both the BACnet and Infinet sides of the tree.

If you want to remove specific configured points from the controller but retain it in the tree, you will need to first delete the BACnet side of the controller from the BACnet tree, then you can delete individual objects (or make changes) from the Infinet tree.

 

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 11052
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of