What amount of memory is used for DPU Resident Individuals in DPU/SCU controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What amount of memory is used for DPU Resident Individuals in DPU/SCU controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2322 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What amount of memory is used for DPU Resident Individuals in DPU/SCU controller

Picard Product_Support
‎2020-10-13 03:31 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:24 AM

Issue

What amount of memory is used for DPU Resident Individuals in the DPU\SCU controller?

Product Line

TAC I/NET

Environment

  • I/NET Seven - Access control
  • DPU7910A, DPU7920, DPU7920 w/DPU48K, and SCU1284

Cause

Need to understand the memory allocation and implications of using DPU Resident settings with both the DPU or SCU hardware devices.

Resolution

To set the Individual as DPU Resident the DPU Res. checkbox needs to be checked in the Individuals editor as shown below (red box) shown below.

DPU Resident Setting.png

 

 

In the table below from TCON300 05/17 Chapter 9-14 shows the memory allocation for a 7910A DPU or DPU7920

DPU7910A-7920.png

 

If you have a selection of between 6000 to 12000 Resident User Individuals (i.e. set as DPU Resident) in the system you can ONLY have between 3262 to 2887 Cached users respectively stored within a properly communicating system.  If the DPU is offline to the Sub LAN Interface (SLI) these cached users will be reduced as the requirement for the DPU storage capacity will need to store 'offline' messages as shown under the "Messages" column.  

 

In the table below from TCON300 05/17 Chapter 9-15  shows the memory allocation for a SCU1284 DPU or DPU7920 w/DPU48K

SCU1284.png

 

If you have a selection of between 6000 to 12000 Resident Users Individuals (i.e. set as DPU Resident) in the system you can have the full quota of 48,000 Cache Users respectively stored within a properly communicating system.  Unlike the DPU7910 or 7920 if the DPU is offline to the Sub LAN Interface (SLI) there is no change to these cached users and there is more 'offline' message storage as shown under the "Messages" column.

For further information on DPU Caching and memory management read from Chapter 9-11 in TCON300-05/17

Labels (1)
Labels:
  • TAC INET
Tags (3)
  • Find more articles tagged with:
  • 2891
  • RobertAndriolo19
  • RobertAndriolo20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore