What BACnet Command priority does a Cyberstation program use in changing value of BACnet points?
  • What BACnet Command priority does a Cyberstation program use in changing value of BACnet points?
  • sesa119747
    sesa119747
  • SangKim
    SangKim
‎2018-09-06 02:36 PM
Cyberstation
Change the value of BACnet points
When you use the WriteProperty() function, you must use the BACnet path of the object for WriteProperty() function.
- If the priority# is given in the WriteProperty() function, it sets the value of the point with the given priority#.
- If the priority# is not given in the WriteProperty() function, it sets the value with priority#16 by default.
When you don't use WriteProperty() function.
- If you use BACnet path ( Ex; BACnetDevices\BCXName\MyNum = 12.340), it sets the value with the priority# that is defined in the attribute of BACnet Command Priority for Cyberstation Programs in the BACnet Preferences.
- If you use Infinity path ( Ex; MyNetworkName\BCXName\MyNum = 12.340), it sets the value with priority# 10 by default.
  • 3498