Webstation Alarm do not show up and give a Unexpected exception has occurred error
  • Webstation Alarm do not show up and give a Unexpected exception has occurred error
  • PeterLarsen
    PeterLarsen
‎2018-09-11 07:32 AM
When you use Webstation to access alarms in a Vista database you get a error in the alarm pane.
TAC Vista
Vista 5.1.x
The $alarmColumns under the root directory has all of the selected columns selected for display.
To get the Webstation alarm pane to display correctly uncheck one of the columns.
This has been noted as a QT6670 and not to be fixed
  • 16078