Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

WebStation timeouts using broadband cellular networks

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • WebStation timeouts using broadband cellular networks
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1057 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

WebStation timeouts using broadband cellular networks

Picard RobertAndriolo Picard
‎2021-06-15 09:42 PM

Issue

  • WebStation connection is unreliable when using a 4G (cellular) connection
  • Auto logoff times are not obeyed 

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation WebStation 3.x
  • Broadband Cellular Networks

Cause

WebStation creates a subscription with the Building Operation server, so it will attempt to connect every 10 seconds.  If this connection is removed/interrupted/ or no longer required for a period of 60 seconds, WebStation will force itself to log out.  This setting is currently fixed and cannot be adjusted.   

Currently, there have been instances where this connectivity issue is seen when using, as shown below, a device with a broadband cellular connection attempting to connect to a Building Operation server that also connected to the same/similar cellular network this is the most common scenario where this issue is seen.

WebStation-Scenario1.png

Resolution

It is recommended not to use these cellular network connections to permanently display Building Operation Server information, especially from mobile devices connecting to the cellular network.  This type of connection should be used sparingly and for quick access to view/check information as necessary.  Connection loss can be expected if you move away from the webpage for more than 60 seconds.  Any lengthy connections to the Building Operation Server are recommended to use a more permanent network connection.  

 

Issues have not been seen when using broadband Internet or a similar connection as shown below to a remote cellular Building Operation Server.  This meaning that the EcoStruxure Building Operation system has remote Internet access via a broadband cellular connection.

WebStation-Scenario2.png

To troubleshoot this further, capture a HAR file using the details provided here How to collect a network trace | Microsoft Docs and reproduce the issue while this debugging window is open within your browser.  Note: This capture must be done at the source; that is where WebStation is running.  This may not be easy to do using a mobile device.  

Send this saved HAR file and the Internet browser version and EBO version used along with connection types to your local support channel. 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • RobertAndriolo21
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore