  • How to calculate the required disk space that will be used by WebReports?
  • How to know if SQL 2008 R2 Express (with Advanced Services) will have adequate storage space for the sites Reporting requirements?
WebReports 1.9 / 2.0
Require the ability to forecast how much space will be required to store and retain data within the Building Operation WebReports database.
The attached Excel Spreadsheets can be used to forecast how much space is needed to store and retain the Building Operation WebReports database.
WebReports_DB Usage Calculator.zip
WebReports_DB Growth Estimator 2.0.zip
Note that SQL 2008 R2 Express only allows a database size of 10 GB, so if your configuration is more extensive than that you should probably consider using the full SQL Server 2008 R2 editions.
As a quick indicator here are the record sizes for each object type stored in the report server database:
Object Type
Size per record (bytes)
WebReports versions <1.8 >1.9
Ext. Trend 140 165
Meter 170 140
Alarm 900 500
Event 400 520