Viewing Events from a particular controller
  • Viewing Events from a particular controller
  • PeterLarsen
    PeterLarsen
‎2018-09-06 03:14 PM
Is there a way to see what someone has done on a particular Xenta controller and what they have changed
Vista
Yes you can select the controller and retrieve the events for that controller.
First locate the controller in the network.
The right click on the controller and select View events
The event viewer will then display all the events from that controller. this will include the old vale and new value is a value has been changed.
The user that made these changes is also logged in the event viewer.
You can use the filter option    then to narrow down on the date range if required.