Very slow to logon to a TAC Vista server using TAC Vista Workstation
  • Very slow to logon to a TAC Vista server using TAC Vista Workstation
  • Jonas_Brissman
    Jonas_Brissman
‎2018-09-06 09:21 AM
Last Updated: Administrator DavidFisher Administrator ‎2019-08-26 11:30 AM
It takes up to 3-4 minutes before a user is logged in to the Workstation.
TAC Vista
TAC Vista 5.1.8
The problem is a combination between a Vista server network and many disabled alarms.
When logging on with a Workstation to a Vista server, the server will read the disabled alarms from the other Vista servers in the TAC Vista network. This is a slow process that can be slowed down even more if there are  hundreds of disabled alarms.
  1. Try to keep disabled alarms to a minimum in a Vista server network.
  2. Don't have unnecessary disabled alarms in the system.
  • 16999