Verifying Xenta Group Bindings in an LNS system

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Verifying Xenta Group Bindings in an LNS system
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1943 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Verifying Xenta Group Bindings in an LNS system

Picard Product_Support
‎2018-09-06 02:22 PM

Issue

Xenta group bindings are used for group communication between Xenta group masters and members.  They also transmit TAC Network Variables between two programmable controllers.  Redoing group bindings is a common troubleshooting technique to address issues with these functions.  However, it can often be time consuming, especially if using LonMaker which requires the Visio drawing to be resynchronized.  Verifying that the Xenta group bindings in the device's address table are correct prior to redoing them can save time on an unnecessary troubleshooting step.

Product Line

TAC Vista

Environment

Vista programmable controllers

LonMaker, NL220

Cause

Checking to see if the group bindings need to be redone instead of always using it as a standard troubleshooting technique can save time.

Resolution

To access the Device Address Table of an application device in LonMaker:

  1. Right-click on the controller in LonMaker and go to Properties.
  2. Go to the Address table tab.
  3. Look at the first two entries (0 and 1) and note the value in the ID column.
  4. Go to another controller in the same group and compare the values in the ID column.
    • Every controller on a network should share the same ID in row 0.
    • Every controller in a group should share the same ID in row 1.
  5. If the group bindings are correct, there is no need to redo group bindings.

 

To access the Device Address Table of an application device in NL220:

  1. Select the application device in the tree
  2. Press Ctrl+A keys or right click on it and select the option Network\Network tables ... in its context menu
  3. Select the tab Addresses
     

 The grid contains one line for each entry in the address table.

  • Index = The index of the address entry
  • MT = Yes if the entry is reserved for message tags connection
  • Type = Type of the entry, Unbound (Not used or "free"), Turnaround, Subnet/Node, Broadcast, Group
  • Size = Size of the group (zero for a large group) and Used only if Type is Group
  • Domain = Domain index (0/1)
  • Mb/Node = Member if Type is Group (not used for a huge group), Node id if Type is Subnet/Node or Unused
  • Repeat timer = Value of the repeat timer 
  • Retries = Retries count
  • Rcv timer = Value of the receive timer 
  • Tx timer = Value of the transmit timer 
  • Gp/Subnet  = Group id if Type is Group, Subnet id if Type is Subnet/Node or Unused
     

Refresh will refresh the table.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4427
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of