Values sent from a Xenta 121 FC/HP via SNVT bindings are not making it to the receiving controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Values sent from a Xenta 121 FC/HP via SNVT bindings are not making it to the receiving controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • LeeCravens
    LeeCravens
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1684 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Values sent from a Xenta 121 FC/HP via SNVT bindings are not making it to the receiving controller

Picard Product_Support
‎2018-09-10 10:30 PM

Issue

Values sent from a Xenta 121 FC/HP controller via SNVT bindings are not making it to the receiving controller. Viewing the outbound SNVT on the Xenta 121 shows a value, but the inbound SNVT on the receiving controller is invalid or a default value.

Product Line

TAC Vista

Environment

  •  Vista
  • NL220
  • LonMaker
  • ZBuilder

Cause

The Node Configuration parameters are set with a send heartbeat of 0 seconds, which tells the controller to never send an update on the output SNVT.  All Xenta 121 controllers come with a default send heartbeat of 0 seconds, so for them to function in an LNS network where they must send data to another controller, the send heartbeat must be set to something greater than 0 seconds.

Resolution

In order to adjust the send or receive heartbeat of a Xenta 121 controller, follow these steps:

  1. Right click on the controller and go to PlugIns > TAC ZBuilder Plug-In.
  2. In ZBuilder, click on the Configuration tab and go to LON > Node. Here the Send heartbeat and Receive heartbeat can be changed.

The following nvo values will require the Send heartbeat be set to a value greater than zero in order to communicate with another controller using a SNVT binding.

nvoSpaceTemp
nvoUnitStatus
nvoHeatPrimary
nvoHeatSecondary
nvoCoolPrimary
nvoEffectOccup
nvoTerminalLoad
nvoEffectSetpt
nvoFanSpeed
nvoEnergyHoldOff
nvoOccSensor
nvoRawDOStatus

 

The following nvi values will default to invalid if they do not receive an update within a specified period of time. For most applications this should be left at zero. If the application must actively poll a SNVT then the receive heartbeat can be set to a value greater than zero.

nviApplicMode
nviSetPtOffset
nviEnergyHoldOff
nviFanProof
nviOccSensor
nviSpaceRH
nviOutdoorRH
nviSpaceIAQ
nviOutdoorTemp
nviSourceTemp
nviAuxHeatEnable
nviSourceFlow
nviComprEnable

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 10993
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore