Valent RTUs with LynxSpring BACnet MSTP controllers go offline about every 30 minutes.
  • Valent RTUs with LynxSpring BACnet MSTP controllers go offline about every 30 minutes.
  • BillNeville
    BillNeville
‎2018-09-06 09:16 AM
After about 30 minutes of communicating fine they will go off line in the AS.
BACnet, AS v1.41
Time sync service running on the Lynxspring JACEs
Restarting the Lynxspring controllers temporarily resolves the offline problem.
Turning OFF the time sync service running on the Lynxspring JACEs permanently resolved the offline problem.
  • 17071
100% helpful (1/1)