Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Using an STR-350/351 as a Menta I/O Module: Menta Macro

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using an STR-350/351 as a Menta I/O Module: Menta Macro
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1756 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using an STR-350/351 as a Menta I/O Module: Menta Macro

Picard Product_Support
‎2018-09-09 10:06 PM

Issue

When using the STR-350/351 as an I/O module in Menta (Options > Device Specification > IO Expansion and Wall Module Table) some programming consideration must be made to keep the occupancy and setpoint in sync between the stat and the program. Both STRIN and STROUT Menta simple blocks should be used for the most robust synchronization.

Environment

  • STR-350/351 as an I/O Module
  • Menta

Cause

The STR-350 takes roughly 30 seconds to recover from a power failure. The Xenta is much faster than that resulting in reading an invalid setpoint from the STR-350 on a power cycle. By storing the last known setpoint in a DELR block with the "backup" option set, the setpoint will be restored (provided the power has not been off longer than 3 days, in which case it would default back to the initial value of the backed up value).

Resolution

Click the pictures of the Menta macro below to download the source file.

Occupancy

To control occupancy from the programmable controller time schedule, the occupancy must be sent to the STR-350. In order to allow for local override commands from the stat, the occupancy must be read in from the STR-350. By allowing the programmable controller to control both the schedule and the override, the stat stays in synch with the program.

Setpoint

The setpoint requires a little bit of extra programming to account for a power failure. The stat will report invalid setpoints for the first 30 seconds, which will cause it to come back in an undesired state. By letting the programmable hold onto the last known setpoint, and write it back to the stat on power up, there is no change in the setpoint after a power loss. Looping the setpoint in/out from the stat keeps everything in synch with the program, including stat adjustments.

Note: This code protects against unwanted behavior following a power failure. A download the Xenta base unit will not trigger the Reset block protection and will cause the stat to go outside the bounds of, and then be limited by, either the high or low setpoint limit. Precaution should be taken following a download to manually reset the setpoint to the desired value. Additional logic for controlling the setpoint remotely could be incorporated into this code.

If these macros are going to be used with a STR-350/351 set in degrees Celsius; make sure to change all initial values within the setpoint range. If the initial values are outside of the setpoint range, then the setpoint will always default back to the last known value.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Attachments
UsingAnSTR350.zip
Tags (1)
  • Find more articles tagged with:
  • 5273
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore