Using a USB-Serial Lead to SDCU a Sigma Controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using a USB-Serial Lead to SDCU a Sigma Controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidChild
    DavidChild
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2041 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using a USB-Serial Lead to SDCU a Sigma Controller

Picard Product_Support
‎2018-09-06 01:22 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-05 09:05 PM

Issue

Your laptop does not have a native serial (RS232) port. Can a USB-to-Serial adapter be used to connect to a Sigma controller via the SDCU utility?

Product Line

Satchwell BAS & Sigma

Environment

  • Satchwell Sigma Controllers
  • SDCU

Cause

Modern laptops typically omit legacy RS232 serial ports in favor of USB interfaces. The SDCU utility requires a serial connection to communicate with Sigma controllers. Without a native serial port, a USB-to-Serial adapter is needed to emulate the required RS232 interface.

Resolution

Yes, a USB-to-Serial RS232 adapter can be used to SDCU a Sigma controller. Follow these steps to ensure proper setup:


🔧 Step-by-Step Instructions

  1. Connect the USB-to-Serial Adapter

    • Plug the USB-Serial lead into your laptop.
    • For first-time use, install the driver provided with the adapter (typically from the manufacturer like FTDI or Prolific).
  2. Verify COM Port Assignment

    • Navigate to:
      My Computer > View System Information > Hardware > Device Manager > Ports (COM & LPT)
      
    • Note the COM port number assigned to the adapter (e.g., COM3).


      ⚠️ This port number may change each time the adapter is reconnected.

  3. Connect to the Controller

    • Use the SDCU lead to bridge between the USB-Serial adapter and the Sigma controller.
  4. Launch SDCU Utility

    • Open the SDCU software.
    • Set the communication port to match the COM port identified in Step 2.
  5. Configure the Controller

    • Proceed with controller configuration as required.

SDCU Cable Pinouts

TinyTake21-09-2023-02-47-39.png


✅ Compatibility Notes

  • Supported Adapters: FTDI and Prolific chipsets are commonly compatible.
  • Troubleshooting Tip: If communication fails, verify driver installation and COM port settings. Try a different USB port if needed.

🔗 Related Articles

  • USB Serial Adapter Compatibility with Sigma
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (3)
  • Find more articles tagged with:
  • 6300
  • CraigEllis23
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore