Using a Door's Card Reader to Inhibit and Enable Alarms

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using a Door's Card Reader to Inhibit and Enable Alarms
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Derrick_Ratliff
    Derrick_Ratliff
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1705 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using a Door's Card Reader to Inhibit and Enable Alarms

Picard Product_Support
‎2020-09-22 08:05 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2020-09-22 08:06 PM

Issue

Using a Door's Card Reader to Inhibit and Enable Alarms

Product Line

TAC I/NET

Environment

I/NET

Cause

Access Initiated Control (AIC) can be used to trigger points based on reader entry.  This is triggered regardless of if the door is open or closed.

Also, when using multiple commands, such as inhibit/enable alarms, one would need multiple readers to trigger the points.  The following process allows you to use the same reader to trigger both the enable, and inhibit alarm function.

Resolution

Create Points:

  1. If you have not done so yet, build a point for the Door Status.( These directions assume that 1= Open and 0 = Closed)
  2. Build an internal point called AIC Trigger.
  3. Create a calculation that keeps this point in the off state

Configure AIC

  1. Create an AIC that will turn the AIC Trigger point on with a reader entry
  2. Assign this AIC to the appropriate door

Create Event Sequences

  1. Create an event sequence called Enable
  2. Create an event sequence called Inhibit
  3. Modify the Inhibit event Sequence
  4. Add lines that will Inhibit each alarm
  5. For the last line, set a delay equal to the strike duration and the type as Skip if non-Zero
  6. Set the point as the Door Status and the Sequence as the Enable Sequence #
  7. Click OK
  8. Modify the Enable sequence
  9. Add lines that will Enable each alarm
  10. Click OK
  11. Click close
  12. Select Edit>Controller>Point Extensions>Event Definition
  13. Double Click on the AIC Trigger Point
  14. Set the Event type to Specified State
  15. Select "Sequence" and set the sequence number as the Inhibit sequence
  16. Select the State/Value as On
  17. Click OK

Results

  1. Entering the door with a valid card read will cause all alarms to go to an inhibit state
  2. After exiting the door and allowing it to close, one can scan a card to enable the alarms. This will take effect after a delay equal to the strike duration.
  3. This process is based on the door position switch being open or closed as the strike duration expires. So that arming the system will only occur if the door is closed.
  4. There is a potential flaw if someone is able to scan a card, enter the room, and close the door before the strike duration expires.  If this happens the system will re-arm itself as the strike duration expires. For this reason, it is important to have as short a strike duration as possible.
Labels (1)
Labels:
  • TAC INET
Tags (2)
  • Find more articles tagged with:
  • 5369
  • RobertAndriolo20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore