Issue
Using Xenta Controllers with a Tridium Jace
Product Line
TAC Vista, TAC IA Series
Environment
- Xenta programmable controllers
- Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B
- Tridium AX / N4 Jace
Cause
By default, the Tridium Jace acts as a network manager which will disrupt controller addresses, SNVT bindings, and Group bindings previously set up in LonMaker.
Resolution
To disable this feature provide these steps to a Tridium Integrator:
- Use Niagara WorkBench
- Connect to Jace
- Under the Services Folder, find "LonNetwork"
- Go to "Local Lon Device"
- Set the "External Config" property to "true"
- Hit "Save"