Using LOYTEC L-IP in TAC Vista Classic Network

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using LOYTEC L-IP in TAC Vista Classic Network
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Anonymous user
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3052 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using LOYTEC L-IP in TAC Vista Classic Network

Picard Product_Support
‎2018-09-07 05:57 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 07:56 PM

Issue

  1. How to use L-IP in Vista Classic network.
  2. Cannot service pin controllers under L-IP in Vista Classic network.
  3. Values in Classic network under multichannel L-IP are showing "Invalid Address" and "No such entity"

Product Line

TAC Vista

Environment

  • TAC Vista Workstation
  • L-IP
  • NIC852

Cause

  1. LOYTEC L-IP needs to be configured as a server and into the smart mode in order to be used in the Classic network.
  2. NIC852 needs to be used with LOYTEC L-IP in the Classic network.

Resolution

  1. Configure L-IP as a web server (How to Configure Lonworks Network Interfaces to Communicate on the IP to a Loytec L-IP Router using ...).
     
  2. Configure L-IP into Smart mode.
    There are two ways to configure L-IP into smart mode.  Flip the DIP switch or using a serial cable (RS232).
    1. Flip the DIP switch to activate the smart mode. The dip switch is at the side of the L-IP next to the Ethernet port. L-IP DIP switch has seven switches.  By default, DIP switch 3 is down and the rest switches are up.


      1. Flip dip switch 2 down to activate the smart mode.


         
    2. Use RS232 serial cable to activate the smart mode. Read more information in the LOYTEC L-IP User Manual Chapter 4.4.2.2
       
  3. Configure NIC852
    1. Open LConfig and go to NIC852 tab (Start/All Programs/LOYTEC Network Interface/LConfig).
      NOTE:  LOYTEC Network Interface package can be downloaded from LOYTEC website, called NIC-LOYTEC Network Interface Software X.X.X
    2. Make sure “Enable device” is checked
    3. Click on “CNIP Configuration”.
    4. Under “Device IP Address” use computer's address and use 1628 as Port number. Under “Conf. Server IP Addr.” Use L-IP’s IP  address and use 1629 as Port number.


       
    5. Click “OK”.
    6. Click on “Test Device”, and should return the serial number
       
  4. Add LIP as a LTA in Classic network.
    1. Right click on the Vista Server and choose “New->Device->Communication Port-LOYTEC”
    2. Name the LTA (for example: LIP).
       
  5. Edit LIP in Classic network.
    1. Right Click on the LOYTEC L-IP (in this example the LIP LTA) just added and choose “Properties”.
    2. Under Communication Settings, click on the arrow and select the available NIC852.



       
  6. Commission the LIP in Classic network.
    1. Right click on the LOYTEC L-IP just added (in this example the LIP LTA) and choose New > Device > LonWorks Network
    2. Name the network (for example: LNS
    3. Right click on the LonWorks Network just added (in this example the LNS network) and choose “Commission and Download”
    4. Select the LonWorks Network (in this example the LNS network) and click the “Start the Selected Operation” button (up-down arrow button on the top)
    5. Click “Continue” when asking for “Continue operation?”
    6. Operation successful message should be displayed.


       
  7. Refresh (F5) the tree in the left panel in TAC Vista Workstation. The L-IP LTA (in this example the LIP LTA) and the LonWorks Network (in this example the LNS network) should turn green afterwards.

Now the L-IP is ready to communicate in the TAC Classic network.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4570
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore