Using Gmail SMTP Server to send alarms and reports via emails in I/A Series G3

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using Gmail SMTP Server to send alarms and reports via emails in I/A Series G3
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4236 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using Gmail SMTP Server to send alarms and reports via emails in I/A Series G3

Picard Product_Support
‎2018-09-10 02:46 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:22 AM

Issue

Unable to successfully use Gmail SMTP server to send out alarms via email from I/A Series G3. 

Various errors can be seen in the console output. Some of the errors are indicated below but they may not be limited to these.

  • Error: BOutgoingAccount could not dequeue persistent email: 550 The address is not valid
  • java.lang.Exception: Valid CryptoService not found

Environment

Enterprise Network Server / Enterprise Network Controller

  • I/A Series G3 version 3.5 and above
  • I/A Series G3 maintenance builds version 3.4.55 and above

Cause

Improper configuration of the EmailService's OutgoingAccount and missing CryptoService in the station.

Resolution

Procedure and properties settings required when using the Gmail SMTP Server:

  1. Add the EmailService and CryptoService to the station's Services folder. If emails are to be sent from an ENC, ensure that the email and crypto modules (and their dependencies) are installed into the ENC.
  2. Add the OutgoingAccount to the EmailService.
  3. In the OutgoingAccount properties, configure the properties indicated below. Leave other properties as their default settings.
    • Hostname: smtp.gmail.com
    • Port: 465 (this is the TCP port SMTP over SSL uses)
    • Account: example@gmail.com
    • Password: Your Gmail account password
    • Enabled: true
    • Use Ssl: true (Gmail requires SSL)
    • Transport: SMTP
    • Use Authentication: true (Gmail requires authentication when sending out emails)
  4. You can test the functionality by right-clicking on the EmailService and selecting 'Actions' > 'Send' to send out an email.
  5. If you are still having an issue with authentication, it may need to allow less secure apps to access your Gmail account. Refer to https://support.google.com/accounts/answer/6010255?hl=en for details. 

Notes:

  1. CryptoService enables the SSL feature in the G3 station.
  2. The crypto module is included in the installation of I/A Series G3 version 3.6 but it was not included in earlier versions. You can download the crypto modules for earlier versions of G3 (crypto 3.4.64 / crypto 3.5.34) from The Exchange Download Center.
  3. Ensure that the station is licensed for crypto. You can look into your license file to check. Below is an example taken from a demo license.
    feature expiration="2012-03-31" name="crypto" parts="ENS-DEMO" ssl="true"
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 6028
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore