Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Using Database Initialization to add a workstation to an existing system results in an error.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using Database Initialization to add a workstation to an existing system results in an error.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AdamSteele
    AdamSteele
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1316 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using Database Initialization to add a workstation to an existing system results in an error.

Picard Product_Support
‎2018-09-06 11:16 AM

Issue

Using Database Initialization to add a workstation to an existing system results in an error.

After inputting all required information on the Workstation dialog, the below error is seen and the Workstation is not initialized into the database.

"Failed to initialize workstation"

Environment

Continuum Cyberstation

BACnet Devices

Cause

Third-party (or our own) BACnet controllers are interfering with the creation of the workstation device object. The BACnet Device ID's are clashing.

All workstations require an ID. If you have a BACnet system, in the Device Node ID field, enter the BACnet ID for the workstation. (Each workstation requires a unique BACnet ID number.) It can be any unique ID number between 1 and 4194302.

Note: In a BACnet network, this ID is unique for workstations and controllers alike and is vendor-independent

Each BACnet Device (including the Continuum workstation's) must have a unique ID that does not conflict with any other device on the same BACnet network.
 

Resolution

You can identify BACnet Device ID's already used within the Continuum Database and then choose one that does not conflict.

  1. Create a Listview looking at Device class with a path type of AllPaths. As a minimum add the following columns; Name, InstanceId, NetworkId, NetworkNumber.
  2. Run the listview. The list it generates is all of the BACnet Devices defined within your Continuum Database.
  3. The last portion of the InstanceId (after the backslash) indicates that Devices BACnet Device ID.

     
  4. You will need to identify a free number that is not being used and change the Device Node ID value you were trying to use in the Workstation Configuration dialog window. With this new Device Node ID that is not conflicting, you should now be able to initialize your workstation successfully.
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 11023
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of